    Default 240v Voltec Charge Station Install

    I have a 30 amp 240v dryer outlet in the basement that is 50' from the garage (about 95' total from panel to garage). Looks like it uses #10 wire— it's unmarked, but definitely larger diameter than #12 by maybe 1.5x.

    Because I have an existing gas line for a gas dryer, I'm thinking of replacing the electric dryer with a new gas dryer, removing the electric dryer outlet (so it cant be used by accident), extending the existing 240v run 50' to the garage, thereby using the existing electric dryer infrastructure for the charger instead.

    Based on what I've read, once the wiring extension is in, I'll need to replace the dryer's 30 amp double breaker with a 20 amp double for the $495 240v 15 amp SPX unit.

    Another variation is the inline switch described by Joule Thief http://gm-volt.com/forum/showthread.php?9599 though that would seem to require a small panel in the garage to install a 20 amp breaker as the 30 amp would be over sized for this charger.

    Yes? No? Have I overlooked anything in the above?

    voltec_lg.jpg
    Cyber Gray, Std Wheels, Black Leather/White Console, Park Assist. Picked up May 2011
    B3320
    Best All Electric Miles: 54.2
    Lifetime: 30,821 miles, 140 MPG, Remaining Oil Life 100%
    Typical Commute: 57-67 miles
    30 day Stats: 1100 miles, 201
    MPG, 82% Electric, 28% gas, Saved 42 gal., 26 kW-hr/100 miles
    VOLT TIPS & SECRETS

  2. #2
    Join Date
    Jul 2008
    Location
    San Diego
    Posts
    6,277

    Default

    Sounds good. No reason to replace the breakers. The breakers protect the wire not the appliance, and the EVSE will work just fine with the lower gauge wire.

  3. #3
    Join Date
    Jul 2009
    Location
    Kitchener, Ontario, Canada
    Posts
    847

    Default

    I'm an engineer that works in the design of appliances and I can say that the breaker protects more than just the wires. Most appliances are tested and designed to work with a maximum overcircuit protection (breaker is an example). Check with SPX and see what the maximum certified overcircuit protection is for their unit. I would guess it's probably 20amps. As for wire there is no harm in having an oversized wire.

    My company has had issues in the past with people connecting our products to oversized breakers (we have won every law suit that may have resulted under these circumstances). If a short occurs in the device the surge energy may be to great for the protection systems in the device if connected to an oversized breaker.

  4.  

    Advertisement

  5. #4
    Join Date
    Aug 2011
    Location
    Seattle Area
    Posts
    152

    Default

    Quote Originally Posted by Steverino View Post
    I have a 30 amp 240v dryer outlet in the basement that is 50' from the garage (about 95' total from panel to garage). Looks like it uses #10 wire— it's unmarked, but definitely larger diameter than #12 by maybe 1.5x.

    Because I have an existing gas line for a gas dryer, I'm thinking of replacing the electric dryer with a new gas dryer, removing the electric dryer outlet (so it cant be used by accident), extending the existing 240v run 50' to the garage, thereby using the existing electric dryer infrastructure for the charger instead.

    Based on what I've read, once the wiring extension is in, I'll need to replace the dryer's 30 amp double breaker with a 20 amp double for the $495 240v 15 amp SPX unit.

    Another variation is the inline switch described by Joule Thief http://gm-volt.com/forum/showthread.php?9599 though that would seem to require a small panel in the garage to install a 20 amp breaker as the 30 amp would be over sized for this charger.

    Yes? No? Have I overlooked anything in the above?

    Attachment 3736
    You're going down the right road. Replace the breaker with a 20 Amp because you don't need the 30 and the 20 provides a better margin of safety if something goes wrong since the charger is intended to be installed on a 20 Amp circuit as stated in the install instructions.

    Do the splice properly for the extended run and verify that your dryer outlet is 2 Hot + Ground before your start. If it's 2 Hot + Neutral you may need to move the neutral to ground in the panel. In many panels these days the electrical connection is going to be identical (neutrals and grounds attach to the same busbar in the panel) and the only change you may have to make to be 100% proper is to wrap green electrical tape around the insulation at each end of the wire to signifiy it's use as a ground.

    The 10# wire at the beginning of the run only helps you in this case as the voltage drop over the whole thing will be slightly lower than if it were 12#.
    Last edited by pauldon; 11-03-2011 at 06:46 PM. Reason: fix typo
    1969 Camaro RS
    1971 Chevelle SS Convertible
    2008 Suburban LTZ
    2012 Volt #1736 produced 8/16. White Diamond Tricoat, Jet Black and Ceramic White leather seats, all options. Last spotted: In my driveway as of 10/17. Finally! See the route it took to get to me.

    Facebook | Twitter

  6. #5
    Join Date
    Jan 2011
    Location
    Illinois
    Posts
    5,434

    Default

    There are two #10 red wires that end in the panel at the breaker with one one on the left side of the double 30A breaker and one on the right side. So both are hot.

    There is one #12 white that connects to the bus bar (insulated from the metal panel box itself) at the top of the panel which is fed by the white service line, so that's neutral.

    There are no ground wires in the panel, nor connectors for them. All wires are in metal conduit, which is grounded via a copper metal strap attached to a water pipe (Do not remove! Electrical connection.).

    So it would seem that capping the white and/or disconnecting it from the bus bar would be an option.
    Last edited by Steverino; 11-03-2011 at 08:27 PM.
    Cyber Gray, Std Wheels, Black Leather/White Console, Park Assist. Picked up May 2011
    B3320
    Best All Electric Miles: 54.2
    Lifetime: 30,821 miles, 140 MPG, Remaining Oil Life 100%
    Typical Commute: 57-67 miles
    30 day Stats: 1100 miles, 201
    MPG, 82% Electric, 28% gas, Saved 42 gal., 26 kW-hr/100 miles
    VOLT TIPS & SECRETS

  7. #6
    Join Date
    Dec 2010
    Location
    Houston, TX
    Posts
    1,481

    Default

    Really no need to go to the effort to remove the outlet for the dryer. If someone accidentally plugs something into the outlet while charging (unlikely -- how many people walk around with a US 240V appliance looking for a random place to plug it in?), it will just trip the breaker.

    Before I had my Blink charger installed, I was using the 110 charger on an outlet that was also connected to my air compressor that I only occasionally used. I usually forgot to unplug the car before starting the compressor, and it just tripped the breaker. Nothing bad happens because that's why the breaker is there.
    Last edited by voltage692; 11-03-2011 at 09:20 PM.
    -----------------------------------------------
    Volt #947 Delivered on 2/25/11 -- Sold!
    240V Blink Installed 10/28/11 -- Returned!

  8. #7
    Join Date
    Aug 2011
    Location
    Seattle Area
    Posts
    152

    Default

    Quote Originally Posted by Steverino View Post
    There are two #10 red wires that end in the panel at the breaker with one one on the left side of the double 30A breaker and one on the right side. So both are hot.

    There is one #12 white that connects to the bus bar (insulated from the metal panel box itself) at the top of the panel which is fed by the white service line, so that's neutral.

    There are no ground wires in the panel, nor connectors for them. All wires are in metal conduit, which is grounded via a copper metal strap attached to a water pipe (Do not remove! Electrical connection.).

    So it would seem that capping the white and/or disconnecting it from the bus bar would be an option.
    Codes and practices vary from region to region as I'm sure you've seen here but if the conduit is an allowed method of grounding there and it sounds like it probably is if they have the conduit clearly grounded and labelled then you can tie your conduit or metal box to the ground in your EVSE. For the unused neutral it's generally allowed to cap off unused wires with a wire nut and I usually wrap the nut and wire with a bit tape too.

    All in all you are in good shape.
    1969 Camaro RS
    1971 Chevelle SS Convertible
    2008 Suburban LTZ
    2012 Volt #1736 produced 8/16. White Diamond Tricoat, Jet Black and Ceramic White leather seats, all options. Last spotted: In my driveway as of 10/17. Finally! See the route it took to get to me.

    Facebook | Twitter

  9. #8
    Join Date
    Jan 2011
    Location
    Illinois
    Posts
    5,434

    Default

    Yes, wrapping the wire nut in electrical tape is cheap extra protection to keep the nut from somehow working loose and exposing the wire. I appreciate everyone's input.
    Cyber Gray, Std Wheels, Black Leather/White Console, Park Assist. Picked up May 2011
    B3320
    Best All Electric Miles: 54.2
    Lifetime: 30,821 miles, 140 MPG, Remaining Oil Life 100%
    Typical Commute: 57-67 miles
    30 day Stats: 1100 miles, 201
    MPG, 82% Electric, 28% gas, Saved 42 gal., 26 kW-hr/100 miles
    VOLT TIPS & SECRETS

  10. #9
    Join Date
    Mar 2011
    Location
    Erin,ON
    Posts
    822

    Default

    I used a #10 wire as well. It will safely meet all the requirements of the charger. If you were using the line for a welder a #8 wire would be better but you won't get the electricity spikes with the charger, like you would with a welder, to be worried about that.
    2012 Volt Topaz Blue Metallic C4773!! aka HAL

    http://www.voltstats.net/Stats/Details/226

  11.  

    Advertisement

  12. #10
    Join Date
    Apr 2011
    Location
    Texas
    Posts
    316

    Default

    Quote Originally Posted by Neromanceres View Post
    I'm an engineer that works in the design of appliances and I can say that the breaker protects more than just the wires. Most appliances are tested and designed to work with a maximum overcircuit protection (breaker is an example). Check with SPX and see what the maximum certified overcircuit protection is for their unit. I would guess it's probably 20amps.
    You are correct and it is 20amp. It's listed in the spec's for the unit.
    ----------------------------------------
    Volt #2243

Similar Threads

  1. 240V Voltec self-install - DONE!!
    By GalinMD in forum Volt Ownership Forum
    Replies: 31
    Last Post: 10-14-2012, 10:39 PM
  2. Replies: 14
    Last Post: 08-04-2012, 07:12 PM
  3. My Voltec 240V plugin install
    By KenEE in forum Chevy Volt Accessories, Modifications, and Hacks
    Replies: 21
    Last Post: 06-12-2011, 01:08 AM
  4. SPX Voltec™ Charge Station EVSE - NEC and UL spec insightful
    By scottf200 in forum Engineering and Design
    Replies: 5
    Last Post: 04-11-2011, 01:50 PM
  5. SPX Voltec 220v charge station (EVSE) does not need a neutral
    By scottf200 in forum Chevy Volt Accessories, Modifications, and Hacks
    Replies: 7
    Last Post: 02-11-2011, 01:09 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts