    Default 120V Portable Charger...

    I'm an electrician and I have a customer who has purchased a 2012 VOLT. The charging unit has two setting, 12A & 8A. When he sets it to 12A the unit displays the "red" light indicating a Ground Fault. If he uses the 8A setting it is better but still, sometimes, gets the same result, "red" light.

    He has used this at other locations and seem to be working just fine on either setting. At his home the electrical source, panel, is ~120' away, 15A #14 wire. Could there be an issue with Voltage Drop causing these results?

    Thank you in advance.

    1793
    Last edited by 1793; 07-04-2012 at 08:43 AM. Reason: added some wording for clarification

  2. #2
    Join Date
    Jul 2009
    Location
    Kitchener, Ontario, Canada
    Posts
    844

    Default

    Quote Originally Posted by 1793 View Post
    I'm an electrician and I have a customer who has purchased a 2012 VOLT. The charging unit has two setting, 12A & 8A. When he sets it to 12A the unit displays the "red" light indicating a Ground Fault. If he uses the 8A setting it is better but still, sometimes, gets the same result, "red" light.

    He has used this at other locations and seem to be working just fine on either setting. At his home the electrical source, panel, is ~120' away, 15A #14 wire. Could there be an issue with Voltage Drop causing these results?

    Thank you in advance.

    1793
    It could very well be voltage drop. But it's odd that the unit is indicating a ground fault. I have attached an image of the page from the Volt manual with the two error lights. If it is indicating a ground fault then it is likely something else. Could you disconnect the breaker and check the resistance between the live and ground? If not the Volt 120 EVSE seems to be fairly sensitive to voltage drop and power quality. If the EVSE is indicating a Voltage out of range error it could be contact resistance at the connections (plug or breaker). Or it could be a combination of a long run and so-so power quality. Can you test the voltage under load? One more thing it might be is a high resistance to ground. If the ground is not very good the Volt EVSE is not happy either.

    2012_EVSE_Indicators.jpg
    Last edited by Neromanceres; 07-04-2012 at 10:00 AM.

    7 August 2012 - 2013 Volt - D3079 - Blue Topaz Metallic - Pebble Beige Cloth - Comfort Package and Safety Package 1 came home.
    https://www.voltstats.net/Stats/Details/1667

  3. #3
    Join Date
    Jan 2012
    Location
    Lakeland Florida
    Posts
    1,272

    Default

    It could be both Voltage drop and the similar resistance on the ground. Your looking at over 240ft round trip on the resistance which will be over 8 volts drop, that way to much for reliable operation. At that length, to keep within the NEC 3% rule you would need that length run to be 10AWG, which would still be near a 3.5 volt drop

    I would suggest running a 6 position sub panel to the garage using 6AWG, this would allow for upgrading to a 240V charger as well in the future.
    Last edited by Henry_FL; 07-04-2012 at 11:07 AM. Reason: corrected values
    2012 Crystal Red Volt #10921 - Plug Powered #76

  4.  

    Advertisement

  5. #4
    Join Date
    Jul 2009
    Location
    Kitchener, Ontario, Canada
    Posts
    844

    Default

    Quote Originally Posted by Henry_FL View Post
    It could be both Voltage drop and the similar resistance on the ground. Your looking at over 240ft round trip on the resistance which will be over 18 volts drop, that way to much for reliable operation. At that length, to keep within the NEC 3% rule you would need that length run to be 8AWG, which would still be near a 4.5 volt drop

    I would suggest running a 6 position sub panel to the garage using 6AWG, this would allow for upgrading to a 240V charger as well in the future.
    Not to argue but #14 wire at 240 feet is 0.61 Ohms. At 12 Amps current the Voltage drop would be ~7.32V (not including contact resistances and assuming 68F temperature). Which is still a little high. #10 wire would get you to within 3% voltage drop (~2.9V @ 12A).

    Edit:
    Found an online calculator as well with some good tips:
    http://www.nooutage.com/vdrop.htm
    Last edited by Neromanceres; 07-04-2012 at 11:00 AM. Reason: Found online calculator

    7 August 2012 - 2013 Volt - D3079 - Blue Topaz Metallic - Pebble Beige Cloth - Comfort Package and Safety Package 1 came home.
    https://www.voltstats.net/Stats/Details/1667

  6. #5
    Join Date
    Oct 2011
    Location
    HAMILTON,NJ
    Posts
    186

    Default

    We get that problem always when the extension cord is too small in size. Use heavy duty cord only.. Shorten teh distance as much as possile.
    Jack Phillips
    Hamilton, NJ
    Vin # 2501

  7. #6
    Join Date
    Jan 2011
    Location
    SE PA
    Posts
    3,480

    Default

    In my garage (well whole house) it looks like I have 14/2 installed with 20A breakers. That may be to local code but I'm going to have a 12/2 drop pulled to the garage, new high-end 20A plug and 15A breaker. In my case, we have 121V in the house (via kill-a-watt) so there isn't much worry about voltage drop here.

    For the OP - I wonder if they used aluminum wiring?

  8. #7
    Join Date
    Jul 2012
    Location
    Kentucky
    Posts
    2

    Default

    Quote Originally Posted by bonaire View Post
    In my garage (well whole house) it looks like I have 14/2 installed with 20A breakers. That may be to local code but I'm going to have a 12/2 drop pulled to the garage, new high-end 20A plug and 15A breaker. In my case, we have 121V in the house (via kill-a-watt) so there isn't much worry about voltage drop here.

    For the OP - I wonder if they used aluminum wiring?
    Wiring is CU.

  9. #8
    Join Date
    Jun 2012
    Location
    UK
    Posts
    34

    Default

    Quote Originally Posted by 1793 View Post
    Wiring is CU.
    The Portable Charger can be used in the standard reduced level function, but the charging time is improved. When choosing 12A (1.5kW) charging function, the 12 Amp LED lights up. If 12 Amp LED is not illuminated, charging rate is limited to a default maximum of 7A (.84kW).

Similar Threads

  1. Portable Solar Charger / Trickle Charger accessories?
    By mmongeon in forum Chevy Volt Accessories, Modifications, and Hacks
    Replies: 15
    Last Post: 08-23-2012, 03:19 PM
  2. Portable SPX 220 Charger Install
    By George S. Bower in forum Volt Ownership Forum
    Replies: 4
    Last Post: 06-10-2012, 10:53 AM
  3. Best Portable 240V Charger Suggestions
    By fixinit in forum Volt Ownership Forum
    Replies: 8
    Last Post: 04-02-2012, 12:57 AM
  4. portable 220 charger, avcon adapter rig
    By chewy in forum Chevy Volt Accessories, Modifications, and Hacks
    Replies: 14
    Last Post: 02-24-2012, 06:33 PM
  5. Leaf 240V charging via the portable 120V EVSE
    By scottf200 in forum Chevy Volt Accessories, Modifications, and Hacks
    Replies: 48
    Last Post: 12-15-2011, 01:30 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts