    I am a proud owner of a 2 week old Chevy Volt. I decided to purchase the 240 Voltec charging station from SPX. I have received it with a thinking I would have someone install it. I got nervous. I figured will my electrician really know what they are doing, the permits, the guarantee...uggg...So I called SPX and I have decided to install through them. Good or bad the total will be around $1,700.... Now...I currently have a 20amp circuit in the garage ready to go but the electrician who did the site assessment recommended I upgrade to a 40 amp. More wiring is required. I was quoted 2 prices. One with the 20 amp and the other with the 40 amp. It is a difference of $300.

    Is going to the 40 amp the better option? I don't know much about electricity but I get all charged up reading this website. (pun here. ) Any thoughts? Stick with 20 or go with the 40?
    Crystal Red Tintcoat #C-6838
    12/9/11

  2. #2
    Join Date
    Nov 2011
    Location
    Millville, PA
    Posts
    51

    Default

    20 amps @ 240v is all the Voltec needs. If you think you might buy a car in the future with a larger battery capacity, go for the 40 Amp service.

  3. #3
    Join Date
    Sep 2010
    Location
    Phoenix, AZ
    Posts
    2,698

    Default

    We went one step further and added a 60 amp sub panel in the garage, currently running 2 SPX 240 volt chargers off that.
    Diamond White #B2140 ecosister plate=SLRRYDER
    Crystal Red #C8885, Red-Rider plate=NO2OPEC
    No gas purchased, fully charged off Solar, OK so I bought some gas to go to Vegas!
    DRIVING for FREE! NO OPEC FEE!

    My TED 5000 power monitoring

  4.  

    Advertisement

  5. #4
    Join Date
    Dec 2010
    Posts
    152

    Default

    40 amp. The 2012 Ford Focus Electric already has a 6.6 kwh charger, which needs the 40 amp service. I'd expect most cars to need (or at least be able to enjoy) 40 amps in the near future.

  6. #5
    Join Date
    Oct 2011
    Location
    Cary NC - central North Carolina just east of Raleigh
    Posts
    208

    Default

    I'd go with 40 amp just for piece of mind. With a 20 amp, things should work, and they should be safe and durable, but you would be using most of the circuit capacity every day for a lengthy duty cycle period. High leve of loading means high stress = potential for problems.

    With a 40 amp circuit, you will have equipment that will never be stressed beyond around half of its rated capacity. If it were mine I'd do the 40 amp circuit. And by the way, I am getting a 240 V charger but not from SPX, and I will have a 30 or 40 amp circuit, not just 20.

  7. #6
    Join Date
    Nov 2011
    Location
    Woodbury, MN
    Posts
    6

    Default

    I bought the Voltec charger from SPX and had a local electrician install it. No problem. Any licensed electrician should be able to do it. And it only cost me $462 to have it installed. SPX would've charged a lot more.

  8. #7
    Join Date
    Jul 2009
    Location
    Kitchener, Ontario, Canada
    Posts
    847

    Default

    I'm an engineer who designs products that are wired by electricians.

    The Volt SPX 240V charger is a 3.3KW unit and is only cETLus approved for use on a 20A circuit. A 40A circuit breaker is oversized and in a short circuit event the breaker may not be able to protect the charging unit. The relays may weld shut and prevent the ground fault protection from functioning properly. The electrician that told you that you could use a 40A circuit direct to the unit is misguided and possibly dangerous.

    Now if you want to install 8AWG wire to handle a 40A circuit in the future that is fine. But the SPX charger needs to be on a 20A circuit breaker max.

    There are other L2 EVSE's out there that are designed to be used on a 40A circuit to take advantage of the higher 6.6KW charging of some other vehicles (Ford Focus EV, Tesla, ... etc). But the Volt SPX charger is not one of them. The SPX Volt charger works to only 15A continuous.

    https://www.homecharging.spx.com/volt/pdf/GM10-463A.pdf
    Last edited by Neromanceres; 12-21-2011 at 08:09 PM.

  9. #8
    Join Date
    Jan 2011
    Location
    Rancho Palos Verdes, CA
    Posts
    2,124

    Default

    Neromanceres #7

    Good advice IMHO. My dryer service, which I took over for the Voltec charger, actually had a 40 amp breaker. My electrician told me the same thing and we switched it out for a 20 amp. I had a similar experience with the SPX installer, telling me that I needed a 40 amp circuit and trying to move me way up market. I gave up on them and had a local guy do it and it worked out fine.

  10. #9
    Join Date
    May 2011
    Location
    Toronto, Canada
    Posts
    51

    Default

    Hey VoltinME, Neromanceres' assessment is completely correct. I went through exactly what you are going through. I went through a lengthy fact finding mission only to find out that GM had given me the wrong advice to go with the 40 amp breaker. My electrician and I had reservations so we dug deeper. Through my Volt advisor, we ended up consulting with a GM/SPX engineer...he said exactly what Neromanceres just explained.

    Heed his advice, and go with the heavier gauge wire (be careful not to go too big or it won't fit into the Level 2 terminal sockets) and a 20 amp breaker.

    Hope this helps. So far the charger has performed great...however, just yesterday I found that when preconditioning at the comfort setting (and high fan setting), the charger experiences a fault part way into the preconditioning session. When I do it in eco mode, the fault does not occur it.

    Figaro

  11.  

    Advertisement

  12. #10
    Join Date
    Jan 2011
    Location
    Portland, Maine
    Posts
    45

    Default Thanks

    Thanks for all your advice!!
    Crystal Red Tintcoat #C-6838
    12/9/11

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts